消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

老年人建筑是否可以采用边墙型喷头

《喷规》6.1.3 湿式系统的洒水喷头选型应符合下列规定:     

     3 顶板为水平面的轻危险级、中危险级Ⅰ级住宅建筑、宿舍、旅馆建筑客房、医疗建筑病房和办公室,可采用边墙型洒水喷头。


这里面没有明确说中危险级Ⅰ级的老年人建筑可以采用边墙型喷头,是否不能采用。

和德 | 2022-12-09 09:02
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

张牙舞爪的张 2022-12-09 11:39 10 [回复]举报

老年人照料设施属于自喷系统危险等级划分中的轻危险级别。边墙、隐蔽、局部应用、消防洒水、PVC—c管都能应用到轻、中|危险等级场所。

关闭

关闭

手机APP下载