丙类厂房内设置办公室

  根据建筑设计防火规范 GB50016-2014(2018年版)3.3.9规定:  办公室、休息室设置在丙类厂房内时,应采用耐火极限不低于2.50h的防火隔墙和1.00h的楼板与其他部位分隔,并应至少设置1个独立的安全出口。如隔墙上需开设相互连通的门时,应采用乙级防火门。

现实中有一丙类厂房,一层是厂房,二层设置办公室(办公室对应的一层区域为厂房),二层有一个独立的疏散楼梯(封闭楼梯间,在厂房一层直通室外,不与厂房联通)。与厂房分隔部分满足分隔要求,问这样的办公室可以设在该厂房二层吗?

漫步 | 2023-06-10 09:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

hnlyplszq 2023-06-10 11:58 00 [回复]举报

一层厂房,二层办公室,面积比例50%对50%?

违反《防火通用》4.3.1.

若比例合适,可以。

漫步   回复: hnlyplszq2023-06-10 15:34

这个有比例要求?规范上没见啊。这是厂房二层,红色区域是办公室,红色区域以外是厂房,与一层厂房直通。整个一层为厂房。

0    0 [回复]举报

hnlyplszq   回复: 漫步2023-06-12 08:39

地方标准,如江苏规定,其占总面积的15%以内。

0    0 [回复]举报

消防网友11731 2023-06-10 14:54 00 [回复]举报

分隔满足规范要求就应该可以,疏散已经满足了

风无心 2023-06-15 22:19 00 [回复]举报

判断办公是否是仅服务与生产的辅助用房,如果是就可以按《火通规》4.2.2条第3款规定设置,如果是其他性质的办公,按照《火通规》第4.3.1规定是不能组合建造的。