消防用电负荷等级为三级负荷的消防设备,配电箱需要设置末端切换装置吗?

any祥 | 2024-06-29 16:08
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

潘天坤 2024-06-29 21:36 10 [回复]举报

建规GB50016没有描述清楚,然后在建筑防火通用规范 GB55037-2022中有明确要求:三级负荷供电的消防用电设备不需要在其配电线路的最末一级配电箱内设置自动切换装置

建筑防火通用规范 GB55037-2022第10.1.6条规定:

除按照三级负荷供电的消防用电设备外,消防控制室、消防水泵房的消防用电设备及消防电梯等的供电,应在其配电线路的最末一级配电箱内设置自动切换装置。

我头发贼黑 2024-06-30 07:59 10 [回复]举报

55037-10.1.6 除按照三级负荷供电的消防用电设备外,消防控制室、消防水泵房的消防用电设备及消防电梯等的供电,应在其配电线路的最末一级配电箱内设置自动切换装置。防烟和排烟风机房的消防用电设备的供电,应在其配电线路的最末一级配电箱内或所在防火分区的配电箱内设置自动切换装置。防火卷帘、电动排烟窗、消防潜污泵、消防应急照明和疏散指示标志等的供电,应在所在防火分区的配电箱内设置自动切换装置。

懒得说 2024-06-30 08:03 00 [回复]举报

三级消防负荷不需要双电源

快乐星球 2024-06-30 21:37 10 [回复]举报

GB55037-10.1.6,除三级消防负荷外的应设置末端自动切换。