我单位设计某厂的循环水系统,生产用冷水池与消防水池共用(有消防水不被他用的技术措施),消防水泵与生产水泵共用泵房。

qhdzlp | 2021-12-03 18:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

龚亮 2021-12-03 20:51 10 [回复]举报

可以

依据规范《消防给水及消火栓系统技术规范 GB50974-2014》4.3.8 消防用水与其他用水共用的水池,应采取确保消防用水量不作他用的技术措施。


既然水池可以共用,水泵房自然也可以共用,不过要满足消防水泵房的平面布置要求。

qhdzlp   回复: 龚亮2021-12-04 11:57

非常感谢您的答复!审图公司提出应按《建规》第6.2.7条的要求对消防水泵进行防火分隔。

0    0 [回复]举报

hahahu   回复: qhdzlp2021-12-06 11:28

1、感觉怪怪的,基本上都是生活水泵房和消防泵房共用的,很多地方审图验收都没提出过疑问。

2、依照这个理解,消防控制室放入监控设备也不行喽。

0    0 [回复]举报

维刚 2021-12-15 22:19 00 [回复]举报

泵房可以合用(油规允许),化工厂的循环水池与消防水池,单独设置!因为,化工厂的循环水有可能存在易燃易爆化工物料,所以建议单独设置!!!