消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防系统配电箱

验收问题:消防系统专用配电箱设有保护开关对吗?

消防网友64510 | 2022-12-28 10:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

陈曲 2023-01-05 09:58 00 [回复]举报

如果是漏保 那不对 如果是短路保护 没问题

潘天坤 2024-06-26 12:08 00 [回复]举报

具体要看保护开关具体保护什么功能

火灾自动报警系统设计规范 GB50116-2013第10.1.4条规定:火灾自动报警系统主电源不应设置剩余电流动作保护和过负荷保护装置
条文说明提到:剩余电流动作保护和过负荷保护装置一旦报警会自动切断电源,因此火灾自动报警系统主电源不应采用剩余电流动作保护和过负荷保护装置保护
民用建筑电气设计标准 GB51348-2019第7.6.3条规定:对于突然断电比过负荷造成损失更大的线路,不应设置过负荷保护
条文说明提及:突然断电比过负荷造成的损失更大的线路,对于民用建筑来讲,主要指消防动力设备如消防水泵、防排烟风机等的配电线路,这些设备安装在水泵房、地下室防排烟机房等潮湿场所,又经常不运行,如果发生电动机轴封锈蚀,启动时间过长,启动电流过大,断路器的过负荷保护可能跳闸,火灾时不能灭火,会造成更大损失,故该线路不应设置过负荷保护,当设置时只能动作于报警
【技术要点】
    为消防水泵、防排烟风机和消防电梯等的配电线路,断路器不应设置过负荷保护,过负荷报警应采用电动机控制回路的热继电器的报警信号
【实施与检查】
    实施:在设计中,非消防负荷的配电线路应设置过负荷保护,以保证配电线路的安全。对于重要负荷的供配电系统的过负荷保护问题,例如消防水泵、排烟风机之类的负荷供电回路只设置电磁脱扣器。需要故障报警应在电动机控制回路设置热继电器报警而不是切断电路
    检查:应审核设计图纸中消防水泵、防排烟风机供电的配电线路,断路器仅设置电磁脱扣器,这些回路有过负荷应采用电动机控制回路的热继电器的报警信号

关闭

关闭

手机APP下载