消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

水泵出水干管设置的压力开关用电接点压力表替代?

各位大佬,请教一个问题,消防水泵的出水干管的压力传感装置,在规范中都是称“压力开关”,但是看到了部分建筑将出水干管的低压压力开关换成了电接点压力表啊,这种设置应该不符合要求吧,虽然都是压力传感装置,但是电接点压力表的触电电流完全达不到启泵要求,就算能启泵也非常不稳定啊。

徐凯雷 | 2023-08-29 16:15
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

陈曲 2023-08-30 11:40 00 [回复]举报

跟触电电流有一点关系 最主要还是误动作几率高 也容易损坏

任重道远   回复: 陈曲2023-08-30 11:57

是的, 规范当中也没有完全明确压力开关的选型。就是不知道这种设计和安装是否符合要求。

一、电接点压力表是一种带触点(直接由表针与设定针组成)的压力表——能指示压力数值。 特点:触点容量很小,只能带动小型继电器或电子元件。触点几乎没有保持的压力范围。

二.低压压力开关—— 特点:是由压力室与弹簧组成的能快速分合的触点系统。能在设定的压力范围之内保持接通或断开,触点容量大,甚至可直接带动小型电动机,带动大型接触器更是不成问题。

0    0 [回复]举报

张治福 2023-08-31 11:41 00 [回复]举报

一般来讲,规范明确的是具备这些功能。而实现这些功能的手段多种多样,就看谁的水平高,谁出得起价钱。

关闭

关闭

手机APP下载