高层办公楼下裙房设置商铺

高层办公楼下的裙房如果设置商铺是否可以按商业服务网点?如果一间跃层商铺总面积超过300平,这个商铺的疏散该遵循什么原则去考虑?例如跃层商铺楼梯的设置,是否一定需要封闭楼梯间;疏散距离、安全出口个数的考虑等问题。谢谢

高旭光 | 2021-01-10 23:34
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

政委 2021-01-11 11:11 00 [回复]举报

商业服务网点 是住宅建筑特有。后面查找建规安全疏散部分。

消防网友78337 2021-01-11 11:48 00 [回复]举报

商业服务网点只针对住宅楼底层一、二层。

公共建筑底层不存在商业服务网点,应按营业厅、高层建筑来考虑疏散问题。

胡工 2021-01-12 14:53 00 [回复]举报

不能按商业服务网点,应按商业建筑考虑,设封闭楼梯间

中轴线 2021-01-12 16:54 00 [回复]举报

既然都是办公楼了,那么下面这论设置什么,它都不是商业服务网点。也就不存在什么300平的概念了。如果裙房与高层有防火墙,那么各自按各自疏散。如果没有防火墙,按同一栋楼来设计疏散。