消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

关于火灾自动报警系统线管暗敷材质

请问公共建筑的火灾自动报警系统暗敷线管是必须要金属线管吗?还是可以用PVC线管

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

szjun 2022-04-21 08:22 00 [回复]举报

火灾自动报警系统设计规范 GB50116-2013 


11.2.3 线路暗敷设时,应采用金属管、可挠(金属)电气导管或 B1 级以上的刚性塑料管保护,并应敷设在不燃烧体的结构层内,且保护层厚度不宜小于 30mm ;线路明敷设时,应采用金属管、可挠(金属)电气导管或金属封闭线槽保护。矿物绝缘类不燃性电缆可直接明敷。

中国制造 2022-04-21 16:35 00 [回复]举报

暗敷,一般设计的时候是这样,为了省钱地上一律使用你说的PVC(水房等潮湿的场所除外),一般现在的PVC都能满足B1级的要求;地下部分属于规范说的潮湿部分,要求金属管,而且壁厚2mm,根据工艺要求,普通JPG管壁厚可能够呛,所以一般都采用JDG管。

乌伤浪人 2022-04-21 19:34 00 [回复]举报

可以采用PVC管。

关闭

关闭

手机APP下载